Pulling Calcs

eds

Senior Member
Location
Kansas
Occupation
Electrician
Never actually have done a pulling calculation, just curious if the number i have come up with is fairly accurate. 730 is my number

Drop out of ct cabinet 3' hit a 90, go 10' hit another 90, go 70' hit a 30, go 120 hit a 30, go 4' hit a 90 rise 4' to panel.
3'' pvc, all underground except to panel and ct cabinet. 3/0 copper thhn/thwn conductors, 4 total. Planning on using a maxis 3k to pull with. Wire to be on 4 individual spinners grouped together.
 
Not really worried about the pull, just have never done a pull calculation on anything
What did you use to calculate the number 730 you've mentioned?

Also when you have a second please update your profile to include your occupation and location. Long time members often had their info deleted when we had a software change a few years ago. Thanks!
 