JohnJ0906 said:To me, CAT 5 is a communication wire. I guess it is the application. I support all wire. Nothing on a grid.
John if the Cat 5 is running data it does not fit the stated scope of Article 800.
800.1 Scope.
This article covers telephone, telegraph (except radio), outside wiring for fire alarm and burglar alarm, and similar central station systems; and telephone systems not connected to a central station system but using similar types of equipment, methods of installation, and maintenance.
If the Cat 5 is being used for voice then IMO it is clearly an Article 800 installation.
Now here is 725s
725.1 Scope.
This article covers remote-control, signaling, and power-limited circuits that are not an integral part of a device or appliance.
IMO that covers data cabling.
That said, in the real world both voice and data are generally run along common pathways right to the same outlets so it just makes senses to treat them the same with using the more restrictive requirements of 800.