transman2
Senior Member
- Location
- Brooklet,Ga.
Is it safe and legal per code to perform a push by with new cables in a conduit that has an existing energized cable.
Funny you should ask but its at a nuclear plant and has been turned over to the owner but the contractor has been doing this as a norm but I recommend them contacting the owner for approval since its a safety related cable. The contractor tends to take short cuts so they don't have to deal with the owner or perform LOTO. Seems like there safety program is weak to me.What's so important that it can't be turned off for a short period?
Funny you should ask but its at a nuclear plant and has been turned over to the owner but the contractor has been doing this as a norm but I recommend them contacting the owner for approval since its a safety related cable. The contractor tends to take short cuts so they don't have to deal with the owner or perform LOTO. Seems like there safety program is weak to me.
your right and I would have thought that to but they don't.I’d like to think a nuclear plant would have detailed safety procedures on performing every type of maintenance.
Sorry but I would totally disagree with that procedure. Totally wrong and dangerous!I don't know anything about the protocols at a nuke but in commercial work this is done all of the time. We usually pull out the EGC and use it to pull in the additional conductors (+new EGC) while the circuits are energized. Using an insulated EGC as a pull line for additional insulated conductors limits the possibly of damaging the existing conductors to near zero.,
Fair enough, you're entitled to your opinion but in 35+ years I've never had an incident while doing this. As I stated earlier this is a very common practice and I don't know of anyone who's ever had a problem in doing it either. It's not like we're jamming a 1/4" metal snake through a live raceway.Sorry but I would totally disagree with that procedure. Totally wrong and dangerous!
I haven't seen a conduit pull that the multiple conductors didn't have some level of entanglement and where pulling new didn't get semi jammed up with the twisted up existing wire. Not sure about live pulls but have done that sort of pull using an existing wire to pul in a new ones, but not always easy for reason mentioned. Haven't experienced any noticeable damage to existing wire so long as fill requirements met and lube is used.I don't know anything about the protocols at a nuke but in commercial work this is done all of the time. We usually pull out the EGC and use it to pull in the additional conductors (+new EGC) while the circuits are energized. Using an insulated EGC as a pull line for additional insulated conductors limits the possibly of damaging the existing conductors to near zero.,
I should have mentioned that we only use stranded wire so even with #10 AWG there is no problem even when the raceway is approaching maximum fill. The EMT maintains the ground connection.I haven't seen a conduit pull that the multiple conductors didn't have some level of entanglement and where pulling new didn't get semi jammed up with the twisted up existing wire. Not sure about live pulls but have done that sort of pull using an existing wire to pul in a new ones, but not always easy for reason mentioned. Haven't experienced any noticeable damage to existing wire so long as fill requirements met and lube is used.
So how are you maintaining the ground connections if you are using the ground wire as your pull string?
I don't know anything about the protocols at a nuke but in commercial work this is done all of the time. We usually pull out the EGC and use it to pull in the additional conductors (+new EGC) while the circuits are energized. Using an insulated EGC as a pull line for additional insulated conductors limits the possibly of damaging the existing conductors to near zero.,
Funny you should ask but its at a nuclear plant ... The contractor tends to take short cuts ... Seems like their safety program is weak ...
... Interestingly one group pointed to that as a proof to not do the 'pull some more' technique while the c'est la vie folks said yeah but that scuffing / skiving was not really that bad. ...