The line side is hot and you have no idea of the actual condition of the connections. The parts could break, a wire could pull out and any or a number of other things could happen. The use of that tool requires arc flash PPE based on the available fault current and the clearing time of the line side OCPD. Given that the clearing time is problably "never" the incident energy could be over 40 cal/sq. cm.If the main disco is open, what on earth would explode from pulling a meter?