Understood and agree. I was asking because you guys seem to be at the top of your games and if 10 people responded and 8 said it usually easier to pull underground than overhead(all circumstances being equal except where the conduit is being installed...and yes more than likely the conduit will be PVC in grade and not PVC in a building so that would be a constant different) I would have it consider putting in a discount...especially if I have 15,000'.
not a good idea to discount wire pulling.
very, very bad idea.
if you have a problem with a pull, and everyone does
at one time or another, usually what happens is it might
get repulled, and you'll eat the cost of the wire.
i walked in on a data center, was the night shift foreman,
and day shift tried to pull in 400' of 500 mcm copper.
with a smaller ground.
off a wemco reel.
without pulling the locking pin on the sheaves out before
starting the pull.
when i showed up, most of the wire was in a huge ball,
in the parking lot. all snarled. they'd spent all day with
it, and still didn't understand what was wrong. by then,
it was a bit late. imagine a 20' ball of wire weighing about
a ton. now, try to untangle it, in the dark. don't nick that
insulation, hear?
they ordered a new wemco full, and repulled with that.
1,600' of 500 mcm, and 400' of 4/0 copper. they paid
us to cut it up and strip it for scrap.
how's that discount feeling now?