I have domestic water booster pump 480V, 3 phase with (3) 15HP motors being fed by single breaker circuit A.
The circuit A feeds control panel which has fuses for each (3) 15HP motors.
I am thinking circuit A is feeder and breaker should be sized based on 430.62(A) however fuse size inside control panel are not know until the control panel actually gets built. The submittal does not have fuse size
So I have fla of 15hp at 480V is 21A. I can use table 430.52 to size that breaker:
(21x1.75 + 21 + 21) = 78.75A
So then am I correct or incorrect feeder breaker size should be 70A?
had similar post earlier but was not sure if control panel had any fuses or not.
The circuit A feeds control panel which has fuses for each (3) 15HP motors.
I am thinking circuit A is feeder and breaker should be sized based on 430.62(A) however fuse size inside control panel are not know until the control panel actually gets built. The submittal does not have fuse size
So I have fla of 15hp at 480V is 21A. I can use table 430.52 to size that breaker:
(21x1.75 + 21 + 21) = 78.75A
So then am I correct or incorrect feeder breaker size should be 70A?

had similar post earlier but was not sure if control panel had any fuses or not.