Seems this is more complicated than I had thought. I'm content to install my GEC knowing it has something important to do with equalizing potential. Good catch on my #6 typo : )
Read the article I posted.
Sam I skimmed over the article - it's not what you think it is, take a gander at it. I had all sorts of things to say, then I read the article, and then kinda just shrugged off the conversation. It all just comes down to different people looking at different aspects of the same principles, IMO.No, It's totally not my first bar-b-que.
I just realized that I really don't understand what the GEC does. Does it act as lightning protection? #6 min for ground rods seems rather small for that. Does it "equalize" something so that lightning doesn't want to hit that point? Does it have something to do with the POCO transformer feeding the service? Seems like I should know the answer to this but I'm unclear on this..![]()
Seems this discussion has gotten out of hand. It is about the GEC, no single-point or multi-point grounding, or lightning either.
The GEC is meant to protect against electric shock. With metal cased appliances and power tools, it is possible to get a tingle or even a lethal shock due to leakage between the hot line and the metal case. The GEC shunts this current to the neutral/ground bus. If a fault occurs, then this shunted current will be enough to trip the breaker.
AFACT, this discussion isn't about fault conditions. Under ideal conditions, there is 0 volts to earth at the main bonding jumper. Under nominal conditions, there should not be more than a few volts to earth at the bonding jumper.It does not matter how many times it connects to the earth, if you have enough current feeding into the grounding electrode it will not remain at the same potentional as the earth a few feet away from it.
The point is earth grounding provides a voltage reference to the system under normal operating conditions.I have no idea what your trying to get across here![]()
There are several advantages to using this single-point design. For example, if a phase-to-ground fault occurs at a piece of equipment along the electrical distribution system, a relatively controlled low-impedance path is provided back to the source. The fault current has limited routes back to the source and does not have the opportunity to diverge to multiple paths, creating parallel circuits. If multiple paths were introduced, the fault current would divide itself among the paths based on the impedance of the circuits.
Perhaps it is just my nature, but this is paragraph two of the article posted. This is nonsense.
I don't see the nonsense, does that mean I am nonsensical?
One path is better as far as stray current problems such as those that cost dairy farmers money.
Are we talking about faults that last for minutes before tripping a breaker? And are we talking about using the earth as a fault clearing conductor?
The earth will not clear a fault via a ground rod.
Yeah like zero ohms.Maybe if you got a super duper good one. :grin:
Yeah like zero ohms.![]()
Why is it that when someone mentions grounding, many automatically think shock-hazard reduction? That is not the only purpose for grounding... especially earth grounding.
I don't know anymore, I am starting to suspect each of us posting to this thread is talking about something different.
.The GEC is meant to protect against electric shock.
.The GEC shunts this current to the neutral/ground bus. If a fault occurs, then this shunted current will be enough to trip the breaker.
... For example, if a phase-to-ground fault occurs at a piece of equipment along the electrical distribution system, a relatively controlled low-impedance path is provided back to the source.