NTesla76
- IA -Driftless Region
- Electrics
Agreed. Concentrate on good and reliable bonding.Why do we even use a GE or a GEC? Wy not include the GEC with the Service conductors and just bond?
If you have qualifying water pipe structural steel or a CEE there is still some benefit. Two rods however is likely useless most the time.Why do we even use a GE or a GEC? Wy not include the GEC with the Service conductors and just bond?
The grounded conductor (the neutral, almost always) is so called because it is grounded on the utility's network as well as on the premises. A second grounded conductor that is out of the reach of ordinary people would be redundant. (Arguably the EGC is redundant inside the home, but it's a different situation with respect to occupant safety.)Why do we even use a GE or a GEC? Wy not include the GEC with the Service conductors and just bond?
What is the benefit of a water pipe electrode? You have to connect it inside the house. That means whatever lightning might be shunted to ground (a dubious idea IMO), is brought from the outside of the house to the inside where it can do more damage.If you have qualifying water pipe structural steel or a CEE there is still some benefit. Two rods however is likely useless most the time.
Ground electrodes won't prevent damage to a direct lightning strike period.What is the benefit of a water pipe electrode? You have to connect it inside the house. That means whatever lightning might be shunted to ground (a dubious idea IMO), is brought from the outside of the house to the inside where it can do more damage.
The main benefit of a connection to a common underground metal water piping system is that is provides a solid metallic path that will prevent damage when the service neutral is lost.What is the benefit of a water pipe electrode? You have to connect it inside the house. That means whatever lightning might be shunted to ground (a dubious idea IMO), is brought from the outside of the house to the inside where it can do more damage.
if that is what it is for why does the code not say so?The main benefit of a connection to a common underground metal water piping system is that is provides a solid metallic path that will prevent damage when the service neutral is lost.
90.1(A)if that is what it is for why does the code not say so?
I guess sorta, but that is not what the GES is for....seems like then it's just a ticking time bomb waiting for someone to work in the piping and THEN fry everything and probably get shocked in the process. If the code writers think a redundant neutral conductor is prudent then maybe they should require one.The main benefit of a connection to a common underground metal water piping system is that is provides a solid metallic path that will prevent damage when the service neutral is lost.
I think you missed the point. The code gives specific reasons for grounding and this is not one of them.90.1(A)![]()
250.4 General Requirements for Grounding and Bonding.
(A) Grounded Systems.
(1) Electrical System Grounding. Electrical systems that are
grounded shall be connected to earth in a manner that will
limit the voltage imposed by lightning, line surges, or unintentional
contact with higher-voltage lines and that will stabilize
the voltage to earth during normal operation.
Just when I thought, I knew something.I think you missed the point. The code gives specific reasons for grounding and this is not one of them.
Code doesn't state the why for majority of it's content.if that is what it is for why does the code not say so?
Yet in this case it does. Curious.Code doesn't state the why for majority of it's content.
What you quoted from NEC earlier doesn't outright say why grounding is required.Yet in this case it does. Curious.
It actually does, and the verbiage is quite clear about that. There may be other things going on there but what it says is pretty clearly the primary reasons for grounding.What you quoted from NEC earlier doesn't outright say why grounding is required.
I can agree the primary reasons are not quite what some maybe expect it to be. Mostly for an earth reference and stabilizing voltage to earth when a high voltage incident occurs.It actually does, and the verbiage is quite clear about that. There may be other things going on there but what it says is pretty clearly the primary reasons for grounding.
The purpose of the building ground rod at the service is to help keep the building at equal potential with earth and does not protect against fault currents or lightning strikes. NEC requires a maximum of #4 CU ground conductor between the service equipment and the ground rod. Lightning protection conductors are braided by design and building wire is not. There is a reason. To protect a building [ not electronics or equipment ] from lightning requires a combination of lightning protection system is required per LPI and NFPA 78.If a ground rod will not clear a fault & provides a back door for damage by a lighting strike, what is their purpose?
being a good neighbor.....? ~RJ~What is the benefit of a water pipe electrode?
I worked in power production in the Air Force ~5 decades ago and I cannot remember getting that low of an impedance to earth. I also was detailed to Fire Alarm Telegraph System maintenance and those clockwork driven numerical telegraph transmitters had to be able to transmit via ground return if there was an open anywhere on it's single wire looped fire alarm box circuit.I would prefer something less than .5 ohm.