Actually, a manufacturer creating a control drawing is a fundamental requirement - see the definition in Section 500.2 and then read Section 504.10(A) in light of that definition.

You know, I have read that section at least a half dozen times and never realized what it actually said.
 
I use the 800H devices with sealed contacts in non-metallic enclosures in Class I, Division 2 areas all the time. They are suitable for that application. The pot will require that the IS barrier be in the non-classified area.

The IS barrier CAN be located in Cl.I, Div.2 location and the pot connected to its 'safe' side THEN can be located in a Cl.I, Div.2 location.
 