hi there,
i am working on a project that is on hold while we wait for a delayed AC combiner box (eaton 600A 3 phase). the manufacture just told our distributor that the equipment won't be ready til December. we quickly had to adjust the design, by putting three 200A or one 200A and one 400A, both totalling 600A (12 of 50A AC output breakers).
while we wait for an electrical engineer's approved stamp, i am wondering how i can land two different size conductors be landed on the load side of the 600A disconnect, and where i can find a reference in the code book to see if that's a safe wiring method. while I appreciate all your response/input, i am going to ignore all irrelevant questions like "why didn't you install one large inverter instead?"
i am working on a project that is on hold while we wait for a delayed AC combiner box (eaton 600A 3 phase). the manufacture just told our distributor that the equipment won't be ready til December. we quickly had to adjust the design, by putting three 200A or one 200A and one 400A, both totalling 600A (12 of 50A AC output breakers).
while we wait for an electrical engineer's approved stamp, i am wondering how i can land two different size conductors be landed on the load side of the 600A disconnect, and where i can find a reference in the code book to see if that's a safe wiring method. while I appreciate all your response/input, i am going to ignore all irrelevant questions like "why didn't you install one large inverter instead?"