I have seen some discussions in the other threads regarding the requirement of AC disconnects on a PV system and it sounds like this is something that is typically up to the AHJ. My question is based off of the assumption that the local AHJ will require and AC disconnect for a particular design.
So with the assumption that an AC disconnect is required I am wondering how many and the location of the disconnects required for a PV system with (3) inverters feeding into a panel. The PV system goes through three inverters which in turn have their AC side connected to circuit breakers in a panelboard. These inverters and panelboards are located remotely from the facilitys building with the utility entrance and system however this panelbaord is grid-tied to the system so is connected to the utility.
My main question here is if the utility required an AC disconnect for such an arrangement where would it need to be located? Would I simply need one disconnect on the output of the panelboard that is connected to the facilitys utility system, or would I need (3) disconnects one for each inverter that is connected on the branch breakers in the panelboard?
So with the assumption that an AC disconnect is required I am wondering how many and the location of the disconnects required for a PV system with (3) inverters feeding into a panel. The PV system goes through three inverters which in turn have their AC side connected to circuit breakers in a panelboard. These inverters and panelboards are located remotely from the facilitys building with the utility entrance and system however this panelbaord is grid-tied to the system so is connected to the utility.
My main question here is if the utility required an AC disconnect for such an arrangement where would it need to be located? Would I simply need one disconnect on the output of the panelboard that is connected to the facilitys utility system, or would I need (3) disconnects one for each inverter that is connected on the branch breakers in the panelboard?