Is there cause for concern and safety with the new Enphase IQ Microinverter with regard to the AC 2-wire trunk cable that has no equipment grounding conductor? Is it a Code violation? 300.3(B)(2)
These inverters will be used on Arrays in both AC Module systems and Microinverter systems.
My thoughts are that the only equipment grounding connection now will be at a single point on listed 2703 array mounting systems. One errant grounding installation and no more equipment ground on the array. Previous microinverter's had more redundant grounding through the trunk cable with 3-wires.
As industry manufacturer's compete for the low cost system advantage, I don't agree with sacrificing the importance of equipment grounding, especially on rooftops exposed to extreme weather conditions over the expected life cycle of these systems.