I have a customer that has a double throw switch for a portable generator after the meter at a panel board and before their 200a panel which is located at the house 100’ away.
We’re installing rooftop PV, and clearly I can’t backfeed that 200a panel if their generator receptacle remains up stream.
I’m wondering how to pull off essentially a three way interlock. For generator breaker to be on, main and PV must be off. For PV to be on, main must be on and generator off.
Any ideas?
We’re installing rooftop PV, and clearly I can’t backfeed that 200a panel if their generator receptacle remains up stream.
I’m wondering how to pull off essentially a three way interlock. For generator breaker to be on, main and PV must be off. For PV to be on, main must be on and generator off.
Any ideas?