I see. so it's talking about 82 amps only. So can I then use a 110 amp breaker as the supply side interconnection to the service conductors?and that's the only inverter, then 705.11(A) requires that the service conductors have an ampacity of 82A.
Of course the conductors upstream and downstream of the upstream-most OCPD on the PV side are subject to other rules for sizing.
Cheers, Wayne