New to PV installations when installing PV systems is the cable requried to be type PV cable or can standard 600V THHN be used?
PV wire is required by code for exposed wiring in ungrounded PV systems (690.35(D)). Otherwise, USE-2 is acceptable. Once you get into conduit, you may transition to THHN-2. You cannot use THHN (or THHN-2) for exposed wiring and never could.New to PV installations when installing PV systems is the cable requried to be type PV cable or can standard 600V THHN be used?
If a conductor is in conduit, it does not have to be PV wire. If it is exposed to sunlight and it's in an ungrounded system, it does.The drawings and specificatons inidcate a local disc. at the PV array on the roof [ungrounded type] and conduit from the disc. on the roof into the building where the PV will be utilized, there was no specificaoitn on the cable type and was not sure if non-pv cable can be provided from the roof mounted disc. sw. to the DC converter located in the building, of if THHN is acceptable to be used on a PV / DC system, the entire run will be installed in conduit?