electrofelon
Senior Member
- Location
- Cherry Valley NY, Seattle, WA
- Occupation
- Electrician
Say i have a service with a single 200A disconnect which is a typical 200A main breaker panelboard. Say i tap the service conductors in the panel, ahead of the main breaker and run them to another service . disconnect. Lets say the GES consists of 2 ground rods and the GEC lands in the original panel on the neutral bar. Can i use the "common location " provision in 250.64 and thus NOT run a GEC tap the the second disconnect? Would it make any difference if this for PV vs a regular 230.40 exception #2 install?