It seems for this, power is in some ways in both directions as on one hand it is sending power to the utility company, but on the other it is sending power back thru to the inverter that shuts down in the event utility power is lost. Thus the question because is it line or load at any given moment. And it would seem any breaker used must be rated for back feeding. And is there a code reference that requires the back feed breaker be secured in place, like I've seen in other applications?It's kind of implicit in the installation instructions. The 'line' side should be understood to be the side which remains energized when the disconnect is opened. Many people new to solar either don't understand that interactive inverters de-energize their outputs when disconnected, or they get confused by the typical direction of power flow, which they should ignore in this case.