I wasn’t aware 2020 code address this issue?
I am also not aware that 2023 code will address this issue or not? Where do you see this?
Is their anywhere in NEC 2020 it address to group the building AC main service disco with main AC solar disco tapped ahead of building main service disco?
I am dealing with same situation and now our AHJ is now trying to modify and put in local amendment that AC solar main disconnect is service disconnect. I am not sure if this is good idea or not.
My comment about the 2020 addressing this issue in 250.25 was in reply to the bonding and grounding part of the question. My comment says that you treat the line side tap for the solar disconnect like a service disconnect for the purposes of bonding and grounding under the 2020 code.
As far as the 2023, I have sat in on a number of Task Group meetings and Code Panel meetings. There was a specific Task Group set up to submit comments on the issue of the line side solar disconnect being a service disconnect. The TG has members from CMPs 4, 5 and 10. However they receied direction from the Correlating Committee that it
WILL be a service disconnect in the 2023 code and the TG is working out the details and language changes needed to accomplish that. It appears that CMP 10 will have purview over the disconnect and the the purview of CMP 4 will start at the load terminals of the disconnect.
However, the issue is not clear in the 2017 code. You work for the AHJ, so you or your boss makes the call.