690.10 Stand-Alone Systems. The premises wiring system
shall be adequate to meet the requirements of this Code
for a similar installation connected to a service. The wiring
on the supply side of the building or structure disconnecting
means shall comply with the requirements of this Code,
except as modified by 690.10(A) through (E).
690.15 Disconnection of Photovoltaic Equipment. Means
shall be provided to disconnect equipment, such as inverters,
batteries, and charge controllers, from all ungrounded
conductors of all sources. If the equipment is energized
from more than one source, the disconnecting means shall
be grouped and identified.
Is a PV disconnect required for a single 100W module in a stand alone system? Just have a small DC load with a 12VDC car battery for backup.
Thanks in advance
What do you mean by a PV disconnect? The term seems to be most often used to refer to the AC disconnect in a grid interactive system.
In your case the only possibility would be a disconnect between the panels and your DC load and charge controller. If the whole system is outside a building I do not see the necessity. If the panels are outside and the rest of the system is inside, you may well need a DC disconnect.
Where is that exception in art. 690.15... Just curious
:thumbsup::thumbsup:The battery also requires a disconnect and is a probably bigger safety concern than the solar module.
I don't see it there either, but the size of the OP's system says to me that it might not even be associated with a building. (But anything is structure, I know....) Quite likely no permit involved. In terms of safety, given the low voltage of one panel and the strictly limited current, I do not see a need.
The MC4 or other connectors in the panel wiring can serve as an isolating disconnect even if they are not rated for load breaking.
As long as you have two or fewer panels or strings of panels in parallel you do not need to fuse the DC input from the panels. But if you do not fuse the DC input you should make sure that the fusing for the battery and the charge controller will collectively protect the panel wiring in the event of a short inside the charge controller that applies battery voltage directly to the input wires.Since this is a 12VDC system I was planning to add type ATC auto type fuses to the battery and load outputs but was not sure about the solar input since it is current limited.
The only suggestion I would have is to rethink the use of a car battery. Car batteries are designed to deliver a lot of current over a short period of time whereas batteries typically used in solar applications are designed to deliver lower currents over extended periods of time. I think you should investigate 12V batteries designed for solar (or golf carts).This system is powering a weather station in a remote location. The controller is a small 10Amp, 12V controller with Solar and battery inputs and a load output. Currently there is no fusing or any disconnects on anything. We are planning on adding some additional load so we are looking at increasing the solar panel from 10W to 100W. Wanted to bring the system up to the latest NEC codes since we were making these changes. Was not sure if the NEC section 690 applied since it was only a 12VDC system but I could not find any exceptions. There are no MC4 connectors on the new or old solar panel but they could be added if this would be a good solution for the required disconnect.
Since this is a 12VDC system I was planning to add type ATC auto type fuses to the battery and load outputs but was not sure about the solar input since it is current limited. Does the NEC apply to this installation? if so, do we need to add disconnects to the battery and solar inputs? Can the auto type fuse be used as the disconnect? Many questions that I cannot determine from reading section 690.
Thanks
The only suggestion I would have is to rethink the use of a car battery. Car batteries are designed to deliver a lot of current over a short period of time whereas batteries typically used in solar applications are designed to deliver lower currents over extended periods of time. I think you should investigate 12V batteries designed for solar (or golf carts).
This system is powering a weather station in a remote location. The controller is a small 10Amp, 12V controller with Solar and battery inputs and a load output. Currently there is no fusing or any disconnects on anything. We are planning on adding some additional load so we are looking at increasing the solar panel from 10W to 100W. Wanted to bring the system up to the latest NEC codes since we were making these changes. Was not sure if the NEC section 690 applied since it was only a 12VDC system but I could not find any exceptions. There are no MC4 connectors on the new or old solar panel but they could be added if this would be a good solution for the required disconnect.
Since this is a 12VDC system I was planning to add type ATC auto type fuses to the battery and load outputs but was not sure about the solar input since it is current limited. Does the NEC apply to this installation? if so, do we need to add disconnects to the battery and solar inputs? Can the auto type fuse be used as the disconnect? Many questions that I cannot determine from reading section 690.