PV Drawing Question

Status
Not open for further replies.

Jimmy7

Senior Member
Location
Boston, MA
Occupation
Electrician
I have a question on a set of drawings for a solar project I just received. Please take a look at the attached drawing. I'm questioning how they came up with the conductors (2 sets of 3- #400 MCM AL, 1- 2/0 AL Neutral, 1 - #1 CU Ground (250.122)) on the PV side of the Solar AC Disconnect. Isn't parallel 400 AL at 75 degree only good for 540 Amps? How do they get a 2/0 Neutral?

1680882189870.png
 
As long as 125% of inverter output current falls between 500 and 540 amps then this falls under the 'next size up rule' 240.4(B). Note it's the same for the 300mcm CU on the line side of the disconnect. There's no standard size between 500 and 600A.

As far as the neutral, it's highly unlikely that the neutral current from the inverters is more than a tiny fraction of the phase conductor current. And see 220.61(A). Most likely the neutral is still oversized. That said, it would be legit to ask for documentation supporting the max loading of the neutral if they haven't provided that. And it doesn't make much sense that they didn't also spec a smaller neutral on the line side of the disconnect.

There's also 705.28(C)(2)*, but they don't seem to be invoking that because the neutral is larger than the EGC. Also perhaps that 15A breaker at bottom is a monitoring load that uses the neutral.

*2020 NEC citation, formerly 705.95(B).
 
On the non-grid side of the 600A disconnect, the neutral is shown as 2/0 Al and the EGC as #1 Cu. Those are both the minimum EGC size for a 600A OCPD, per Table 250.122.

Cheers, Wayne
Ah, right, I didn't notice the different material or check the table.
So that seems like they're invoking 705.28(C)(2). Maybe they litterally just forgot to do that on the other side.
 