Site Details: 150A Single Phase Service
Customer needs around a 30kW PV system to cover 100% annual.
Proposed Solar AC Interconnection = 132.5 A (After 1.25 correction)
My question is that I will be doing a load side meter tap to interconnect this system into the Electrical system of the building. What are some of the issues that I should be looking at as far as the service? I will be replacing the existing feeders from the meter and putting them in a New 200A disconnect with 150 A fuses for the Main Service Disconnect. Come out of that disconnect into a gutter to house my Tap/Interconnection of the PV. Then come out of the gutter and re-feed existing 150A Main Breaker in Main panel. Obviously doing the same on the PV side with disconnects and fuses to protect this portion as well. Is there something in the Code that I may be missing?
-Bryan
Customer needs around a 30kW PV system to cover 100% annual.
Proposed Solar AC Interconnection = 132.5 A (After 1.25 correction)
My question is that I will be doing a load side meter tap to interconnect this system into the Electrical system of the building. What are some of the issues that I should be looking at as far as the service? I will be replacing the existing feeders from the meter and putting them in a New 200A disconnect with 150 A fuses for the Main Service Disconnect. Come out of that disconnect into a gutter to house my Tap/Interconnection of the PV. Then come out of the gutter and re-feed existing 150A Main Breaker in Main panel. Obviously doing the same on the PV side with disconnects and fuses to protect this portion as well. Is there something in the Code that I may be missing?