I have a 120 208 three phase MDP. 1200 amp bussing. We could do a supply side connection but would rather not if there is a way around it.
The MDP has no main breaker and is 25 years old and located in a large church. We would like to keep this equipment for the expenses of replacement make this project a non starter.
My back feed breaker will be 300 amps. My buss bar is 1200 but no main breaker exists or is able to be installed. Is there a way to install my backed breaker when no main exists.
Currently, in the MDP there is 700 amp breaker feeding some more distribution equipment. a 200 amp breaker feeding a panel. and 2. 100 amp breakers feeding other equipment. A total of four handles to disconnect the entire service.
My guess is that I can not install a pv breaker in this situation. because..... A total of 1100 amp can be pulled through the bussing before any on the four load breakers would trip. plus the current on the back feed breaker 240 amp MAX I. would exceed the buss bar rating. Plus there is room for more load breakers to be added increasing the total load beyond what is there now.
Thought?
Thanks
Thought?
Thanks