They aren't at all ridiculous. PV is weird and different. It turns out that it is very hard to energize both sides of a breaker (UL 1741), but just turning off the service doesn't mean the building is dead. Killing the power in a battery-backed, grid-interactive system is HARD. The good news is that having a power outage is equally hard -- my monitoring system tells me when the neighbors don't have electricity. That or they are all standing out front (waiting on me to come out and gloat

)
The local fire department came by on a fund raiser / petition drive and I offered to have them over to give them a lesson in "How To Turn Off PV". The guy who stopped by my house had never seen so much electrical gear on a residence -- some of which cannot be turned off, period.
There's the PV / grid interconnect (60A 2P), PV disconnect (60A big red handled gadget), battery DC disconnect (2 x 175A DC), and inverter output (60A 3P -- another big red handled gadget). All those have to be turned off. Even with all that, the 2800 watts DC on the roof is still hot, unless the sun isn't shining. Some arrays make serious voltage even when the sun isn't shining just from street lights or moon shine -- I have a "low voltage" array -- about 110 volts DC open circuit and it makes about 20 volts or so from the street lights and moon shine. Some arrays run close to 600 volts and in Europe they run close to 1000 volts.
There are so many signs because there are so many things to possibly kill you.