Can OCPD/Fuses be mounted in a combiner box on the roof under PV Modules? This is for a micro inverters install with enphase inverters. The question is about the fuses being readily accessible.
That would clearly not be readily accessible, as you'd need to remove obstacles and use a tool to get to them. Even with hypothetical module clamps that could be removed without a tool, that would still require the removal of obstacles, thus not readily accessible. It would still be accessible, because removal of a module is reversible, but not readily accessible. In my opinion, I would recommend against this location. I'm aware that opinions are irrelevant for enforcing code-compliance.
With that in mind, combiners are on rooftops all the time, many of which you need a portable ladder to access. You'd be using a portable ladder anyway to troubleshoot the reason why the fuse blew, but still on principle it isn't readily accessible. There are also plenty of combiners sold with enclosures that require a screwdriver to open. Granted, the practice originated before the tool use clarified the definition of readily accessible, but combiners that need screwdrivers to open are still built today, even when specifically built for NEC2014 and later. So I don't know how this is supposed to square with OCPD's in general needing to be readily accessible.