At 10 AM on a sunny day, an operating grid-connected inverter suddenly shuts down. Five minutes later, it comes back on, only to shut down again after a few seconds. It continues this cycle until 3 PM at which point it remains on for the rest of the day. The most likely cause of this problem is
1. The utility voltage has exceeded the IEEE 1547 maximum limits for this time period.
2. The utility voltage has below the IEEE 1547 maximum limits for this time period.
3. The wiring between the inverter and utility connection is undersized.
4. The wiring between the inverter and utility connection is oversized.
This was asked at the end of the year review.