wwhitney
Senior Member
- Location
- Berkeley, CA
- Occupation
- Retired
So in theory you could have a 240V service where the utility provides 264V consistently, and you'd be unable to install any interactive inverters, as their voltage window is also limited to 264V?Yes, utilities in general have a responsibility to keep the voltage within a window near nominal so that peoples appliances and devices function and don't fry. My understanding is that broadly speaking under IEEE standards this is within +10% and -12%. Inverters generally follow the same standards.
I guess that problem is not easy to get rid of in theory, as even if the utility standard were revised to +8% to -12%, if you had enough DG exporting simultaneously, that DG could push the grid voltage up over 2%. Although perhaps in practice, that would be usually be enough margin and it would hard to get enough DG to exceed 2% grid voltage rise?
Any pointers to a good case study/explanation of Hawaii's situation and rules? They have this problem and stricter rules in place to deal with it, right?
Thanks, Wayne