Hey PV experts, I would like to get your input on a PV system for my own house.
I purchased the house I grew up in from the family estate and in the process of doing a major remodel with additions. Hopefully I will be able to afford move in when completed. I had to leave 50% of the exterior wall framing for the city to consider it a remodel. The remainder of the exterior walls, all interior walls and the entire roof structure were replaced.
Anyway, I plan to install a PV system as part of the work. I work around PV systems everyday but never do any installs or pay much attention to what is being installed. Usually we do all the electrical work on a project and a separate PV contractor comes in at the end to install the system.
I’m planning to install roughly a 10KW system. In doing online research I was thinking of using LG panels with SolarEdge inverter/optimizers.
My longtime salesman at my primary wholesale supply house connected me with a sales person at their solar division branch. He said that their main line was Trina but they could get LG if that is what I preferred. He ended up connecting me with his manager since the system was for my house and his manager could discount the material more. After speaking to the manager, he said that they are not authorized for LG sales. He said he could get the panels through another wholesaler but if I ever had a warrantee claim it could be an issue. He asked if I would be willing use Panasonic panels instead of the LG.
I don’t see as much info online on the Panasonic panels compared to the LG but what I have read they seam to be pretty good panels. The LG’s I was considering were either the 350 or 360 watt panels and the Panasonic’s are only 330 watts. From what I’m seeing the price per watt of the Panasonic’s is going to be less than the LG’s so the system would be less expensive with only a minor reduction in output.
So my main question is what are your thoughts of Panasonic panels compared to LG?
My other question is making sure I understand 705.12.
My plan was to install a 200 amp meter main then feed a 400 amp bussed panel next to it. The reason for the 400 amp panel is to allow the 10Kw PV system plus connecting Tesla or some future similar batteries to the system. The 400 amp buss will provide plenty of cushion for the PV system and batteries to stay under the 120%.
The Square D meter mains used in my area all have a main breaker with an 8/16 circuit buss bar then lugs on the bottom. Normally when sizing service equipment we allow for the future PV. We frequently have 30+ branch and feeder breakers in the service panels so the back feed PV and main breaker is limited to 120% . In my case if I don’t install any breakers in the service panel portion I don’t believe I need to worry about the combined utility plus PV supply since there is no way it could overload the buss bars. I would just need to keep the combined feeds of the 400 amp panel under 120%.
I would like to put my A/C and a couple other larger loads in the service panel instead of the 400 amp panel incase I do add batteries in the future. I would not want a large automatic load on the batteries so placing it before the gateway is a better choice.
If I understand 705.12(12)(B)(2)(3)(c) correctly as long as the combine rating of the branch/feeder breakers in the meter main are less than 200 amp I should be ok. Am I understanding this correctly?
Thanks!
I purchased the house I grew up in from the family estate and in the process of doing a major remodel with additions. Hopefully I will be able to afford move in when completed. I had to leave 50% of the exterior wall framing for the city to consider it a remodel. The remainder of the exterior walls, all interior walls and the entire roof structure were replaced.
Anyway, I plan to install a PV system as part of the work. I work around PV systems everyday but never do any installs or pay much attention to what is being installed. Usually we do all the electrical work on a project and a separate PV contractor comes in at the end to install the system.
I’m planning to install roughly a 10KW system. In doing online research I was thinking of using LG panels with SolarEdge inverter/optimizers.
My longtime salesman at my primary wholesale supply house connected me with a sales person at their solar division branch. He said that their main line was Trina but they could get LG if that is what I preferred. He ended up connecting me with his manager since the system was for my house and his manager could discount the material more. After speaking to the manager, he said that they are not authorized for LG sales. He said he could get the panels through another wholesaler but if I ever had a warrantee claim it could be an issue. He asked if I would be willing use Panasonic panels instead of the LG.
I don’t see as much info online on the Panasonic panels compared to the LG but what I have read they seam to be pretty good panels. The LG’s I was considering were either the 350 or 360 watt panels and the Panasonic’s are only 330 watts. From what I’m seeing the price per watt of the Panasonic’s is going to be less than the LG’s so the system would be less expensive with only a minor reduction in output.
So my main question is what are your thoughts of Panasonic panels compared to LG?
My other question is making sure I understand 705.12.
My plan was to install a 200 amp meter main then feed a 400 amp bussed panel next to it. The reason for the 400 amp panel is to allow the 10Kw PV system plus connecting Tesla or some future similar batteries to the system. The 400 amp buss will provide plenty of cushion for the PV system and batteries to stay under the 120%.
The Square D meter mains used in my area all have a main breaker with an 8/16 circuit buss bar then lugs on the bottom. Normally when sizing service equipment we allow for the future PV. We frequently have 30+ branch and feeder breakers in the service panels so the back feed PV and main breaker is limited to 120% . In my case if I don’t install any breakers in the service panel portion I don’t believe I need to worry about the combined utility plus PV supply since there is no way it could overload the buss bars. I would just need to keep the combined feeds of the 400 amp panel under 120%.
I would like to put my A/C and a couple other larger loads in the service panel instead of the 400 amp panel incase I do add batteries in the future. I would not want a large automatic load on the batteries so placing it before the gateway is a better choice.
If I understand 705.12(12)(B)(2)(3)(c) correctly as long as the combine rating of the branch/feeder breakers in the meter main are less than 200 amp I should be ok. Am I understanding this correctly?
Thanks!