Is there an industry stadard for the size of PV Wire? Where can you go to find this? It is not listed in the NEC. I need to do some conduit fill calcs with for PV Cable.
Measure the diameter of the actual cable and calculate the cross-sectional area (CSA). If it is not round, measure perpendicularly across the widest surface points and calculate cross-sectional area as if that measure were the diameter. If you do not yet have the cable, you may be able to obtain the dimensions off the manufacturer's web site.Is there an industry stadard for the size of PV Wire? Where can you go to find this? It is not listed in the NEC. I need to do some conduit fill calcs with for PV Cable.
I don't know that I would call it a standard, but #10 is widely used for home runs.Is there an industry stadard for the size of PV Wire? Where can you go to find this? It is not listed in the NEC. I need to do some conduit fill calcs with for PV Cable.