Re: PVC Conduit between panelboards
Morning all,
I took a look at the code section again (300.3b) did some reseach, talked to some folks. Here is what I found:
The fundamental requirement is that single conductors from one circuit shall be grouped together to mitigate the parasitic effects of magnetic and electric fields generated by current flowing thru a conductor.
One of the ways to achieve conductor grouping is to use raceways etc. If raceways etc are used, all conductors from that circuit shall be contained therein. That's what 300.3b says.
There are other ways to keep conductors in close proximity to achieve conductor grouping, driven by the environment in which they exist such as including them in straps or staples depending on conductor size etc.
The cleanest, easiest most uncontroversial way to achieve grouping is to use conduit or similar. I am told that this method is easiest to inspect as the inspector does not need to judge workmanship, proximity, bend radius etc.
Use conduit and presto zingo - engineering requirement is met!
I am glad I joined this forum!