Take time to check with the fire marshall in your area. I know there is a fire code about surface mounted p.v.c. because of the toxic fumes they omit when burned.
In places of assembly. That's about it.chicar said:I know there is a fire code about surface mounted p.v.c. because of the toxic fumes they omit when burned.
I agree 100% as a contractor.mdshunk said:Hey, home inspectors create a lot of work for electricians. Go with the flow... it's to your benefit. If they call out otherwise legal double-taps, want to see a 60 amp service upgraded, or GFCI's added in a 1950's home, so be it. As long as someone agrees to pay for the work to be done, I don't care who "discovered" it in the first place.
MVanB said:Is PVC (Sched 40/80) an allowable conduit, according to current NEC, for surface installation within an attached residential garage space as an alternative to EMT?
MVanB said:If OK, In it's use for general purpose lighting and receptacle circuits, and it being NM, are the rules the same as for EMT conduit (other than the joints having to be glued)?
.
RUWired said:Yes as long as not subject to physical damage. Then either schedule 80 or another type of metal raceway.
Type nm cable is allowed, but the conductor fill, depending on the size of the raceway, is limited to just one cable. Same rules apply to emt as well.
Rick