PVC Conduit Repair/ Split Pipe

Status
Not open for further replies.
Location
Mississippi
Occupation
Electrician
Does anyone have any experience with pvc pipe repair kits? I would need full 10’ sections. Project is a sports field the site guys are undercutting the home side 15’ deep so all pipe has to be removed and replaced. I am trying my best to reuse wire and pipe.


Sent from my iPhone using Tapatalk
 
6e84a582c3367c0414afd0ae4de0befc.jpg

c2330053533151b3fd400135e6b06bdb.jpg



Sent from my iPhone using Tapatalk
 
I haven't figured out exactly what you are doing.
Are you repairing conduit only without removing the wire?

We've done it before, but stagger cut the wires, slid on good pipe to the point we will install an oversize conduit repair kit. Splice and heat shrink. Install the repair kit. These are repairs on 1/4 mile conduits.

If it is doable pull out the wire, replace the conduit and pull it back in. That's where the expansion joints come in handy.
 
shouldn't one of those wires be green?
Looks like #4 or larger.

250.119(A) Conductors 4 AWG and Larger. Equipment grounding conductors 4 AWG and larger shall comply with 250.119(A)(1) and (A)(2).
(1) An insulated or covered conductor 4 AWG and larger shall be permitted, at the time of installation, to be permanently identified as an equipment grounding conductor at each end and at every point where the conductor is accessible.
 
We are temporarily removing the wire and pipe so the can undercut the surface 8’. We will reinstall when they are adding the fresh fill.


Sent from my iPhone using Tapatalk
 
We are temporarily removing the wire and pipe so the can undercut the surface 8’. We will reinstall when they are adding the fresh fill.


Sent from my iPhone using Tapatalk
I'd likely pull conductors, that way all they can damage during excavation is the pipe and it can be easily pieced together again if that happens.

Trick is probably replacing it without increasing length of conductor needed. Might even be wise to design additional pull/splice boxes that may not been there before (or even as mentioned in ground Quazite boxes) to allow for this kind of thing.
 