Good answer tyThis is my possibly failed logic for the maximum permitted length of a raceway without an expansion fitting.
Example:
Two exterior enclosures with concentric KO's with a straight run of PVC in between. The length of the PVC is limited by the NEC because the expansion or contraction of the PVC over 1/4" can damage the enclosures.
100° temperature change so we'll use the maximum length of PVC without an expansion fitting of 7' as Augie stated.
7' of PVC installed when it's 0° F, expands 1/4" when 100° F. Everything good no damage to enclosures.
7' of PVC installed when it's 100° F, contracts 1/4" when 0° F. Everything good no damage to enclosures.
7' of PVC installed when it's 50° F, expands 1/8" when 100° F. Everything good no damage to enclosures.
7' of PVC installed when it's 50° F, contracts 1/8" when it's 0° F. Everything good no damage to enclosures.
14' of PVC installed when it's 50° F, expands 1/4" when 100° F. Everything good no damage to enclosures.
14' of PVC installed when it's 50° F, contracts 1/4" when it's 0° F. Everything good no damage to enclosures.
This is my possibly failed logic for the maximum permitted length of a raceway without an expansion fitting.
Example:
Two exterior enclosures with concentric KO's with a straight run of PVC in between. The length of the PVC is limited by the NEC because the expansion or contraction of the PVC over 1/4" can damage the enclosures.
100° temperature change so we'll use the maximum length of PVC without an expansion fitting of 7' as Augie stated.
7' of PVC installed when it's 0° F, expands 1/4" when 100° F. Everything good no damage to enclosures.
7' of PVC installed when it's 100° F, contracts 1/4" when 0° F. Everything good no damage to enclosures.
7' of PVC installed when it's 50° F, expands 1/8" when 100° F. Everything good no damage to enclosures.
7' of PVC installed when it's 50° F, contracts 1/8" when it's 0° F. Everything good no damage to enclosures.
14' of PVC installed when it's 50° F, expands 1/4" when 100° F. Everything good no damage to enclosures.
14' of PVC installed when it's 50° F, contracts 1/4" when it's 0° F. Everything good no damage to enclosures.
TyAugie said any run more than 7' so that would include the two runs at the top along the peak and the run to the right where the two LB's are.
In almost all cases, I have only needed on fitting in a straight runs, however, I did a greenhouse and found the need of 2 in a single run. I had to argue with the installing "electricians" to even needing any, since the concept eludes most hack electricians.I was at a high school softball field that had a PVC run from the dugout along the top of the fence to the outfield. I don’t know what it was used for, but on a hot summer day, it looked like strand of cooked spaghetti. No expansion joints.
What makes you think this is any less arbitrary than many other code sections? And I don't know that it is specifically "damage" to enclosures as the popping out or straps, pulling the wire, etc. Remember, we could be talking 2" or more of expansion on longer runs.This is my possibly failed logic for the maximum permitted length of a raceway without an expansion fitting.
Example:
Two exterior enclosures with concentric KO's with a straight run of PVC in between. The length of the PVC is limited by the NEC because the expansion or contraction of the PVC over 1/4" can damage the enclosures.
The box damage scenario is just one example as it was a non-exhaustive list. The fact is that for some reason it was decided that the PVC raceway installation can handle 1/4" of expansion or contraction without damaging the system. My issue is with how that 1/4" calculated as demonstrated by my example.And I don't know that it is specifically "damage" to enclosures as the popping out or straps, pulling the wire, etc. Remember, we could be talking 2" or more of expansion on longer runs.
few minutes is probably fine? how long does it take it to cool down when you heat it for bending reasons?if I pull a pipe out of a cold shop then install outdoors in warm weather how long does it take that pipe to accumulate- problem long after I am done— the. What temp do I go with?…
Or the opposite- guess we have tk heat scan the pipe before install and right on each pipe- lol
The NEC never addresses this issue. The manufacturers selection charts only show the full range of minimum to maximum.It isn't clear if that length change is _total_ (minimum expected temperature to maximum expected temperature) or _relative_ to the temperature at installation.
You don't get situations of uninsulated/unconditioned buildings and high temperature especially near ceiling level on a sunny day?I was just stating whatever government body picks it temperature because of the ambient temperature does not mean the pipe is that so there’s gonna be a change in shrinkage or gain from the pipe to the temperature outside I was just pointing out the hypocrisy I live in such a mile climate we never use expansion points..,
I’ve been coming to the conclusion that this NEC book is like 10% safety and the rest of is garbage design issue “” not life safety
If you have long expansion fitting and only 1" of calculated change in length, you have some room to play with and wouldn't necessarily have to install at mid range of the fitting.The temperature at the time of installation only applies to where to set the expansion joint. Lets say your your temp range is 0deg-100deg and you install at 50 deg.
So the expansion is calculated at a 100deg change in temp. You install at 50 deg which is half way of the expansion range. So if the total expansion is 1" and you install at 50 deg the joint has to move 1/2" in either direction