wwhitney
- Berkeley, CA
- Retired
I'm curious about the language in 352.44 that requires expansion fittings only for "a straight run between securely mounted items such as boxes, cabinets, elbows, or other conduit terminations." That would imply that a run with elbows (that are not securely mounted) could be allowed to thermally expand and contract without an expansion fitting.
However, the support requirements of Table 352.30 mean that the PVC conduit will be constrained every 3-6 feet (for sizes up to 3"). So in the case of "fixed end - long straight run - elbow - short straight run - fixed end", the short run will be supported within at least 3-6 feet of the elbow. If that support doesn't allow transverse movement, the entire longitudinal expansion or contraction of the long run has to be taken up as a transverse deflection in that 3-6 feet of conduit. I would think this could lead to excess bending force on that 3-6 feet of conduit, and/or excessive angular deviation of the elbow.
So are there supports for PVC conduit that would allow both longitudinal movement of the conduit as well as some transverse movement in one direction? Maybe a piece of unistrut with a clamp that could move back and forth in the unistrut, between stops.
Cheers, Wayne
Cheers, Wayne