dedbrk
Member
- Location
- Washington
I have a mortuary chapel with PVC conduit in the slab feeding PVC floor boxes all of which is slab on grade. 518.4(C)1 states where concealed in floors with a 15 minute finish rating I can do this. Am I incorrect in assuming this? We plan on using brass covers. For the life of me I cannot find a UL listing for fire ratings on a standard floor box. I can find UL fire ratings on poke thru floo boxes all week long, but nothing on standard floor boxes. I can only assume that if a poke thru box is rated for 2 hours with a brass cover then surely a floor box in slab on grade with a brass cover would be the same. I can't find documentation of such. Am I heading in the wrong direction? Any help would be greatly appreciated. Most situations don't turn out favorable when I start assuming things