Are you permitted to use these boxes with a terminal adapter and a metal locknut?

511SYKBvcUL._SL1200_.jpg
 

jap

Senior Member
Occupation
Electrician
The chances of a locknut becoming energized in a completely PVC surrounding would be slim to none in my book.


JAP>
 

Chamuit

Grumpy Old Man
Location
Texas
Occupation
Electrician
Why do the locknuts need to be bonded? If I ran LTNM flex in and used an NM connector (with a metal locknut), I wouldn't have to bond it.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The chances of a locknut becoming energized in a completely PVC surrounding would be slim to none in my book.


JAP>
I agree and I feel the same way about a pan head mounting screw inside of the but those aren't permitted either.

Maybe I'm overthinking this. I'm assuming that any metal part within the box would be required to be bonded.
 
Last edited:

Chamuit

Grumpy Old Man
Location
Texas
Occupation
Electrician
Not trying to be a smart aft, but, do you bond the cover screws? They are actually on the outside where they can be touched.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Not trying to be a smart aft, but, do you bond the cover screws? They are actually on the outside where they can be touched.
I'm looking for feedback so nothing wrong with thinking outside of the box. The cover screws cannot contact the conductors inside of the box so there is no issue with them.
 

Chamuit

Grumpy Old Man
Location
Texas
Occupation
Electrician
I'm looking for feedback so nothing wrong with thinking outside of the box. The cover screws cannot contact the conductors inside of the box so there is no issue with them.
10-4. Don't know if this applies, or is legal, I have used a PVC reducer bushing into a PVC coupling with cement to secure pipe coming into a PVC box. 1x3/4 bushing into 1"coupling with 1x3/4 bushing to conduit. pretty watertight.
carlon-conduit-fittings-e950lj-car-64_145[1].jpg
 

jap

Senior Member
Occupation
Electrician
I agree and I feel the same way about a pan head mounting screw inside of the but those aren't permitted either.

Maybe I'm overthinking this. I'm assuming that any metal part within the box would be required to be bonded.

Not sure what you mean by this.

JAP>
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Not sure what you mean by this.

JAP>
You cannot drill a hole in the back of the box and use screws to mount it.

314.43 Nonmetallic Boxes. Provisions for supports or other mounting means for nonmetallic boxes shall be outside of the
box, or the box shall be constructed so as to prevent contact between the conductors in the box and the supporting screws.
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
I agree and I feel the same way about a pan head mounting screw inside of the but those aren't permitted either.

Maybe I'm overthinking this. I'm assuming that any metal part within the box would be required to be bonded.
The reason the screws inside are not allowed is it affects the sealing of the box, water can enter at those points.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The reason the screws inside are not allowed is it affects the sealing of the box, water can enter at those points.
The code section I posted in post #12 states that the reason is "to prevent contact between the conductors in the box and the supporting screws".
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
So what section would require bonding of the locknut? One could, of course, use a grounding locknut if it is required to be bonded.