Are you permitted to use these boxes with a terminal adapter and a metal locknut?
TA's use metal locknuts, can they be used in a PVC box where the locknuts will not be bonded?Is this a trick question? PVC TA?
I agree and I feel the same way about a pan head mounting screw inside of the but those aren't permitted either.The chances of a locknut becoming energized in a completely PVC surrounding would be slim to none in my book.
JAP>
I'm looking for feedback so nothing wrong with thinking outside of the box. The cover screws cannot contact the conductors inside of the box so there is no issue with them.Not trying to be a smart aft, but, do you bond the cover screws? They are actually on the outside where they can be touched.
10-4. Don't know if this applies, or is legal, I have used a PVC reducer bushing into a PVC coupling with cement to secure pipe coming into a PVC box. 1x3/4 bushing into 1"coupling with 1x3/4 bushing to conduit. pretty watertight.I'm looking for feedback so nothing wrong with thinking outside of the box. The cover screws cannot contact the conductors inside of the box so there is no issue with them.
I agree and I feel the same way about a pan head mounting screw inside of the but those aren't permitted either.
Maybe I'm overthinking this. I'm assuming that any metal part within the box would be required to be bonded.
You cannot drill a hole in the back of the box and use screws to mount it.Not sure what you mean by this.
JAP>
314.43 Nonmetallic Boxes. Provisions for supports or other mounting means for nonmetallic boxes shall be outside of the
box, or the box shall be constructed so as to prevent contact between the conductors in the box and the supporting screws.
The reason the screws inside are not allowed is it affects the sealing of the box, water can enter at those points.I agree and I feel the same way about a pan head mounting screw inside of the but those aren't permitted either.
Maybe I'm overthinking this. I'm assuming that any metal part within the box would be required to be bonded.
The code section I posted in post #12 states that the reason is "to prevent contact between the conductors in the box and the supporting screws".The reason the screws inside are not allowed is it affects the sealing of the box, water can enter at those points.
One problem with the PVC box adapter is that it is irreversible. To have an all-plastic solution that can be reversibly disassembled, I'd recommend a plastic locknut on a PVC male adapter.I am sure you already thought of this but what about a box adapter
Then no lock nutCARLON E996E 3/4 PVC BOX ADPT | Gordon Electric Supply, Inc.
CARLON E996E 3/4" PVC BOX ADAPTERwww.gordonelectricsupply.com
Are you permitted to use these boxes with a terminal adapter and a metal locknut?
That's interesting ,,,,, and makes no sense to me.You cannot drill a hole in the back of the box and use screws to mount it.