PVC pipes for Duct Banks

Status
Not open for further replies.
Those cables are probably direct burial rated anyhow, so my answer is: Just thick enough to hold the concrete until it cures.
 
Those cables are probably direct burial rated anyhow, so my answer is: Just thick enough to hold the concrete until it cures.

And thick enough not to crack while the concrete guys walk all over it installing their rebar cage and during the pour. That's the reason we've gone to schedule 80 recently.
 
Just a matter of reference, we use schedule 80 for that reason as well.

Don't know of any code requirement as to a thickness.
 