We are talking the metallic locknut on a pvc connector
It was regards to post #12
We are talking the metallic locknut on a pvc connector
Yes, it that not what Don stated?It was regards to post #12
and A(3) states that electrical conductive material likely to be energized shall be bonded. Really do we really think that the locknut is likely to get energized and if it did it would be inside the box. Where is the danger?
I don't think that there is any question that a locknut is "equipment" per the Article 100 definition. I cited 250.4(A)(2) and not (A)(3) because (A)(2) does not contain the "likely to be energized" wording. (A)(2) applies to all "equipment".
Yes, it that not what Don stated?
Where metallic plugs or plates are used with nonmetallic enclosures, they shall be recessed at least 6 mm (? in.) from the outer surface of the enclosure.
My quote was from 2011, but there was no change in that section from the 2008.Yes, But I was reading in the 250.4 sections for "Locknuts on a Non-Metallic system to be bonded"..could find it thats why I asked if it was a code change in 2011 but i was not even sure if don was quoting from 2011..