PVC use indoors

Status
Not open for further replies.

Carultch

Senior Member
Location
Massachusetts
3/4 PVC can be up to 3 feet from box to first support as a general rule, and every 3 feet afterward.

Is there any particular reason why the distance limit from termination to the first support is 3 ft across the board for ALL non-flexible circular raceways, whereas the span limit is a function of type and trade size?

I would think that for conduits requiring spans smaller than 10 ft, the distance limit to the first support would shrink proportionately to the allowable span. For instance, with a 5 ft is the span limit, I would expect to see 1.5 ft as the distance limit to the first support. Cantilevers are generally between 30% and 40% of beam spans, for the same structural performance, so I would think a similar concept would apply to the structural integrity conduit systems.
 

kwired

Electron manager
Location
NE Nebraska
Is there any particular reason why the distance limit from termination to the first support is 3 ft across the board for ALL non-flexible circular raceways, whereas the span limit is a function of type and trade size?

I would think that for conduits requiring spans smaller than 10 ft, the distance limit to the first support would shrink proportionately to the allowable span. For instance, with a 5 ft is the span limit, I would expect to see 1.5 ft as the distance limit to the first support. Cantilevers are generally between 30% and 40% of beam spans, for the same structural performance, so I would think a similar concept would apply to the structural integrity conduit systems.

No idea where they come up with those distances, same for the 1 foot to first support for most flexible raceways, which is sometimes difficult to comply with, when maybe 2 feet would still seem pretty reasonable.
 