PVC weatherproof panel connector

Status
Not open for further replies.

kwired

Electron manager
Location
NE Nebraska
It does have ko's on the top, I called generac to ask for a recommendation but they said it was my choice.
Like I said, not very likely this is even an outdoor rated enclosure if it has KO's in the top wall, so take that into consideration.

If it is an opening designed for a bolt on hub, that is different - use appropriate hub.
 

growler

Senior Member
Location
Atlanta,GA
Does it have KO"s in the top wall? If so probably not an outdoor rated enclosure to begin with.

That doesn't sound right. Knock outs in the top of an outdoor rated panel?

I agree and think the OP should double check the rating of this enclosure.
 

patricknola

Electrical contractor/Generac Dealer
Location
new orleans, La, United States
Occupation
Electrical contractor.
It does have ko's on the top, I called generac to ask for a recommendation but they said it was my choice.
That doesn't sound right. Knock outs in the top of an outdoor rated panel?

I agree and think the OP should double check the rating of this enclosure.
I just opened the box it came in and the only ko's are in the back. I'm guessing I'm going to have to punch the bottom .
 

Coppersmith

Senior Member
Location
Tampa, FL, USA
Occupation
Electrical Contractor
Yes Meyer's hub. But don't screw a PVC male adapter into it. That's not allowed. Use a close nipple followed by a female adapter. Put your pipe into that. The reason is the male adapter has straight threads. The Meyer's has tapered threads.
 