PVC/XLPE - THHW

Status
Not open for further replies.

Cloud

Member
Location
PH/VN
Hi All,

If you say the cable has PVC/XLPE insulation, does it means it is already applicable for outside use or comply THHW/THHN cable type?
Cable types according to NEC are THHN, THHW, RHW. My understanding is that PVC/XLPE is just type of insulation material, only to validate the "T" of the code. CMIIW.

Thanks!
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
If it only has PVC/XLPE markings, it is not suitable for use in an NEC application. It must have one of the insulation types shown in Article 310 or be one of the cable types recognized in various Chapter 3 Articles.
 