Yes, heat can be an issue but something the engineer should have addressed in the design phase of the project to insure that the cables will be capable of carrying the current and if any future anticpated load there is a lot of items that need to be know also, is it encased in concrete, what is the fill, if you are running under a road for a significant distance there will be additional concrete, what is the RHO of the soil / concrete / asphalt, and the depth is important too as the deeper you go the harder it is to disipate the heat, the IEEE Brown Book also has some good information on this regarding cable sizes, duct bank configuration and load factor percentages all this comes into account when designing a large underground duct bank with multiple circuits. Hope this helps.
Another question for everyone if you install MV cable in a duct bank with sched.40 pvc the pvc is only rated for 90degree so what do you utilize when installing MV cables with 105degree operating temperature and a max of 250degree for an emergency rating?What type of conduit do you install?