I believe Table 310.15(B)(17). I would see Article 396 also.
Yes your right according to that table I should be good with number 6
At the very least terminal temp. 110.14(C) only permits us to use 310.15(B)(16) to determine minimum size. So to otherwise comply, a higher temperature transition remote to the terminal enclosure would be necessary.Just keep in mind termination temperatures and voltage drop.
110.14(C)..."Table 310.15(B)(20): (formerly Table 310.20) Ampacities of Not More Than Three Single Insulated Conductors, Rated Up to and Including 2000 Volts, Supported on a Messenger, Based on Ambient Air Temperature of 40°C (104°F)"
(1) Equipment Provisions. The determination of termination
provisions of equipment shall be based on 110.14(C)(1)(a) or
(C)(1)(b). Unless the equipment is listed and marked otherwise,
conductor ampacities used in determining equipment termination
provisions shall be based on Table 310.15(B)(16) as
appropriately modified by 310.15(B)(7).
Ignorant Brit strikes again.What size quad Plex aluminum do I need for 100 Amp over head feeder for subpanel, and we're do I find it in the NEC thanks
Four single insulated aluminum conductors (perhaps one bare, depending on who's selling, who's asking) twisted into a cable without a sheath.Ignorant Brit strikes again.
What is quad Plex aluminum?
Thank you kindly. It isn't something I have ever seen.Four single insulated aluminum conductors (perhaps one bare, depending on who's selling, who's asking) twisted into a cable without a sheath.
Just do a Google image search for "quadruplex cable"...Thank you kindly. It isn't something I have ever seen.
The only application I've come across using aluminium conductors are the bus bars on high current rectifiers.
Perhaps I should have said not ever seen used.Just do a Google image search for "quadruplex cable"...
Perhaps I should have said not ever seen used.
Mostly we use stranded copper conductors for installations, typically not less than 2.5mm^2 and 1.0mm^2 flexible for the internal control wiring in panels.
Perhaps I should have said not ever seen used.
Mostly we use stranded copper conductors for installations, typically not less than 2.5mm^2 and 1.0mm^2 flexible for the internal control wiring in panels.
One would need termination method rated for the application I guess, otherwise what good is it to have all those other tables if we are stuck with termination temps from just one of them?110.14(C)...
One would need termination method rated for the application I guess, otherwise what good is it to have all those other tables if we are stuck with termination temps from just one of them?
I agree.One way to take advantage of those tables is to terminate those conductors to larger conductors with connectors listed for those temperatures.