Quad Plex

Status
Not open for further replies.
One would need termination method rated for the application I guess, otherwise what good is it to have all those other tables if we are stuck with termination temps from just one of them?
Derating.


It's either that or learn of inexpensive ways to do TTL transitions. :happyyes:
 
Note that since triplex and quadplex are not specifically listed in Table 396.10(A) some inspection authorities do not permit the use of those cables for installations covered by the NEC.

It is my opinion that you can make a case that list item 6 (Other factory-assembled, multiconductor control, signal, or power cables that are identified for the use) would permit the use of triplex or quadplex, but you really need to check with your inspection authority before using it.
 
Status
Not open for further replies.
Top