What is the purpose of these breakers? I'm looking at a 120/208 volt, 3 phase, 4 wire panel with several of these:
To provide more circuits than spaces allow for.What is the purpose of these breakers?
IMO that would violate the breaker listing. They're also common trip so if one of the poles trips it will trip the other.Do these breakers allow you to remove the bracket that pairs the breakers? So you can operate them as 4 individual circuits?
No need; you can buy them that way, with or without the inner pair linked.Do these breakers allow you to remove the bracket that pairs the breakers? So you can operate them as 4 individual circuits?
Hadn't I just said that?It allows 2-2 pole breakers in a 2-1" slots.
No. If you look closely, that specific one states that both pairs are shown as “Common Trip”, so they are each a true 2 pole breaker and the poles are internally linked.I was wondering why the 2 outer breakers are paired, and the 2 inner ones are paired, but I just realized it's because of the phasing. if you pair two on one end of the quadplex, they will be on the same phase and you won't get 208 volts.
Do these breakers allow you to remove the bracket that pairs the breakers? So you can operate them as 4 individual circuits?