Quazite / In ground fixtures

Status
Not open for further replies.

zooby

Senior Member
Location
Indiana
Occupation
maint. electrician
I am going to look for myself but thought I might ask and see if there is a code I missed or just a best practice----------Do connections inside a quazite enclosure or even in-ground fixtures HAVE to be of the water proof type? I am mostly referring to wire nut. Thanks for any input.
 
Yes, and the wire nuts have to be listed for wet locations. No more using regular wire nuts and pouring some scotchlock or silicone in them.
 