codequestion
Banned
- Location
- MD, USA
I have a question regarding NEC 2014 240.21(B)(2). I have tap which is over 10' long and adding fused safety switch 400 amps off of existing wire way. The tap conductor size is 1 set of 600kcmil. I have following questions:
(A) Tap feeder conductors sizes are adequate per NEC 2014 240.21(B)(2)?
(B) Tap feeder conductors terminate in a single 400A fused safety switch is that per ENC 240.21(B)(2)?
(C) They are being contained in a 4" conduit. However, 240.21(B)(2) number 3 says in an approved raceway or by other approved means. Would 4" conduit be approved means to protect from protection? If not then what would be approved raceway?
(A) Tap feeder conductors sizes are adequate per NEC 2014 240.21(B)(2)?
(B) Tap feeder conductors terminate in a single 400A fused safety switch is that per ENC 240.21(B)(2)?
(C) They are being contained in a 4" conduit. However, 240.21(B)(2) number 3 says in an approved raceway or by other approved means. Would 4" conduit be approved means to protect from protection? If not then what would be approved raceway?