Re: Question about Bonding Structural steel
I am confused....
250.53
Grounding electrode SYSTEM installation
In this section, paragraph (C) it tells you what to do if a bonding jumper is used to connect the electrodes together.
But,
250.64
Grounding electrode conductor INSTALLATION
In this section, paragraph (C) states that the GEC shall be continuous, and in paragraph (F)
To Electrode(s), it states that
a GEC is permitted to be ran to any electrode OR to one or more individually (I can run one GEC for several electrodes or one GEC for each).
Therefore,
When I compare the two sections, I read it this way: when running GEC to the electrodes, I need to follow 250.64 and make them continuous(whether I run one or several GEC's.
Yet, 250.53 tells me what to do when I use a Bonding Jumper between electrodes.
However,
My only hang up with 250.53 is that it doesn't say I
can use bonding jumpers in this fashion, it just tells me what to do
if I use a bonding jumper.
Besides,
250.53 (B) describes the spacing requirements for made electrodes. It then states that when two or more of these made electrodes are
bonded, they are considered one electrode.
(this is where I see it is fine to add more acorns and 'jumper' to your ground rods for additional rods, but only for 'made' electrodes)
Although,
250.50 states that all available electrodes shall be bonded together.
And,
250.53(D) states that when
supplementing the underground water pipe electrode, that the supplemental electrode may be
bonded at
any convenient point.
Consequently,
I am still confused
Roger, IWire, I know what that drawing shows. I just have a problem with how I read things with all the shalls and shall nots. I haven't seen where it says what the picture shows. Let me know if I am missing something, please.
Thank you.