Marketing hype. And I say this as a person that mostly prefers to install Square D as well.
Square D is most of what I normally see, seen many failures of bus to breaker connections on them. Seen very few "classified" QO breakers in my lifetime as well, never seen one fail, but then haven't seen enough of them to have a good chance of seeing that happen either.
Plug on breakers in general are going to have a risk like that. Bolt on - no so much if tightened properly, but over time connections still can get compromised.
I do not dispute that QO breakers fail in QO panels. In fact all brands have a history of burning up, even bolt ons. My point is that when the breaker does not match the panel, you have no clue if it will hold up as well as the matching one.