I have four sets of motor feeder conductors in a conduit, a total of eleven wires. Two of the motors are interlocked with the other two. In other words, only two will run at any one time. Does this eliminate the necessity of derating all conductors to 50% of their ampacity because of Art. 310 "more than three current carrying conductors in a conduit"? I will never have more that six current carrying wires in the conduit at one time, so, shouldn't I be allowed to only derate to 80%? It is my understanding that the code rule addresses the cumulative affect of all conductors under load and producing heat and therefore reducing the current carrying capacity of the wire. I have not been able to find a code section that directly addresses this situation.
Please let me know your opinions.
Thanks