ggunn
PE (Electrical), NABCEP certified
- Location
- Austin, TX, USA
- Occupation
- Consulting Electrical Engineer - Photovoltaic Systems
Their policy is that they do not allow any third party connections in their CT enclosures, and we run into that a lot with utilities. Throwing code at them doesn't make any difference; with utilities we have to play by their rules or not play. It can be very frustrating, but that's just the way it is. I don't know why you keep wanting to wrestle with me over this; maybe your experience with utilities is different but this is mine.What exactly is the policy? I guess they could state something like "supply side PV interconnections shall not be made in the CT enclosure". But then seems like you could just call it 230.40 exception #2, add another set to a MB combiner panel, and connect load side to that using the sum of all OCPD excluding the OCPD protecting the busbar rule.
I was in a meeting with another utility a couple of weeks ago where we had them dead to rights. They were failing us on inspections where they had nothing in the NEC to support their position, but when we pointed that out to them, they just said "we invoke our right to write exceptions to the NEC, so we do that here and now on this issue". End of discussion. Their way or the highway. Frustrating? You betcherass.