My house has a GE Load Center with 4 breakers, all feeding subpanels. I'm assuming this is within code even though there isn't a MAIN breaker considering it's within the 6 disconnect rule??
If there is a ground fault, short circuit downstream of the 4 breakers, that particular breaker will trip.
My question is, if the main feeder short to ground, what trips? POCO?
Lastly, they bonded the nuetral and ground both in the meter enclosure and in the GE main load center which is 8 inches away. Is that right? I thought they were only to be connected at ONE point?
Threephase
If there is a ground fault, short circuit downstream of the 4 breakers, that particular breaker will trip.
My question is, if the main feeder short to ground, what trips? POCO?
Lastly, they bonded the nuetral and ground both in the meter enclosure and in the GE main load center which is 8 inches away. Is that right? I thought they were only to be connected at ONE point?